As far as I know disinfection cycle cannot be triggered from the MMI or via P1/P2, but you can set DHW on/off, DHW temperature target, and boost on/off. |
Beta Was this translation helpful? Give feedback.
-
|
On my EBLA, I can modify DHW on the Madoka or MMI or via HA, and the changes become available in all. But it might differ per system. Do you see manual changes back in HA? |
Beta Was this translation helpful? Give feedback.
-
|
Thanks I can modify the DHW temp but it doesn't seem to go any higher than 52c. Are you able to set the temperature to say 65c and the immersion kick in to reach this temperature? |
Beta Was this translation helpful? Give feedback.
-
|
Can you change the DHW temp on the MMI to more than 52C? I can set the DHW via MMI or HA to 75C ([6-0E], large tank). It may not start heating immediately due to hysteresis settings [6-08] and anti-recycle settings ([8-02]-[8-04]) but eventually it does. |
Beta Was this translation helpful? Give feedback.
-
|
Not sure which version you are running, there was an issue with field setting history capture, can you retry with newest P1P2MQTT-bridge firmware and restart the Daikin after you installed the new firmware to see if the max value gets corrected? |
Beta Was this translation helpful? Give feedback.
-
|
The P1P2 seems to work the same as via the MMI. I can increase the tank temperature target temperature to 65C however I find the daikin never reaches this, it gets to 50c and turns off, even if I have boost on. Feels like a Daikin issue to me. |
Beta Was this translation helpful? Give feedback.
-
|
Would it work dynamically scheduled a disinfection cycle using the field settings? |
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
-
Just wondered if anyone knew if it was possible to trigger a disinfection cycle programmatically. e.g. When electricity price is very low on Octopus Agile.
Beta Was this translation helpful? Give feedback.