Replies: 1 comment
-
|
Great question. MPC ("Model Predictive Control") in BT works on 5-minute steps with a 30-minute prediction horizon ( The cost function it minimizes is roughly: With the defaults:
Practical consequence: MPC strongly prefers continuous moderate heating over bursts, because bursts create overshoot risk (8× penalty) and require larger valve changes. For a heat pump this matches the most efficient operating regime — heat pumps prefer steady moderate output over on/off bursts. The predictor uses the learned |
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
-
Hej all,
i am running the MPC alorithm for some days now together with my heat pump. The Setup is with Sonos TRVs with Direct Valve control and it is generally working like a charm.
But to what goal does the MPC optimize?
To keep the temperature stable by heating in bursts or by setting the valve % so that it just stays steady state? With my heatpump i prefer if all the radiators and the floor heating are moving between 40% and 60% valve opening. if they are higher consistently i will change my heating curve to adjust it back, the same if they are lower. I try to aim for a steady stae in the Heatpump and the valves
Now i am observing that some rooms are in (or close to) this steady state, while others open the valve for 10ish minutes every hour.
Basically all rooms carry a Type 22 radiator that behave simmilar, yet in the Workaway one i get these bursts....
Is that local Maximums the MPC optimizes towards. Is there a way to motivate it to go for more open valves. Or is this more a PID behaviour i should look for? I also rather have it a bit to warm / cold and have the valves open/close more gradual....