Just use the min_cycle_duration option, possibly together with the min_off_cycle_duration. |
Beta Was this translation helpful? Give feedback.
-
|
Thermostat doesnt control heat pump. It runs on fixed outlet water temp and 5 rooms has own thermostats on under floor heating and they control valves on the heating circuits. For longer periors I mean it runs 24/7 on minumum load as it takes like 15-20min to heat up at -15C. |
Beta Was this translation helpful? Give feedback.
-
|
I'm not sure you're asking in the right place for what you want to achieve? By your description the heatpump controls itself based on water outlet temperature, independent of any room thermostats. Do you have any control over the heatpump today? or only room thermostats? |
Beta Was this translation helpful? Give feedback.
-
|
My immediate thought is that the best way to solve your issue is an automation that increases the set temperature on one or more thermostats when your heatpump load reaches a defined lower current load. You could then have another trigger at a higher load that reverts your thermostats setpoint to your actual desired value. |
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
-
I have air to water heat pump and wish to adjust minimum heating to keep pump operating longer periods for better efficiency. I would use external controller or mayby automation to allow small over heating.
Beta Was this translation helpful? Give feedback.