Recording Power connections #12912
Replies: 2 comments 1 reply
-
They represent the individual feeds into the PDU. Think of a power feed as a circuit breaker that supplies power to you. A power panel is just a grouping where power feeds are located together. In a typical data centre, there would be two power feeds into each rack - an A and B feed - and Netbox allows each power feed to be optionally associated with a rack (it's mandatory to associate it with a power panel though). Then you'd connect each power feed into a PDU device (to its power port), and then connect the power outlets on the PDU device to the power ports of the other devices in the rack. I don't fully understand what you've modelled, because you mention PDUs but haven't said how you've connected them. Normally a PDU would have one power port (inlet) and multiple power outlets linked internally to that power port, and then the power outlets would connect to power ports on your servers. (For a similar recent case see #12902) For your CSV: to import power feeds, if you want to associate them with a rack, you need to use the name of the rack. It doesn't matter if the slug is r203 or the database id is 23, it must have name of (say) "R203", and I presume must be in the same site. (Slugs are mostly unused in Netbox, although there are cases you can use them for query filtering in the REST API). Similarly, the name of a rack is only unique within a Location (a.k.a. "rack group" originally), so you may need to specify both the Location Name and the Rack Name to identify it uniquely.
I believe it's because the name of a power panel is only unique within a site, so the combination of (site_name, power_panel_name) is needed to identify it. Aside: I've been trying to document the power features in Netbox in more detail, especially with regards how it calculates overall power utilization from individual device power draw. The gory details are in #12837. |
Beta Was this translation helpful? Give feedback.
-
Residential/Home Use Case: One Circuit Breaker → Multiple DevicesI'm encountering the same limitation mentioned by @CvR42, but in a residential/home lab context rather than a datacenter. The current one-to-one relationship between power feeds and device power ports doesn't align with real-world residential electrical installations. The Real-World ScenarioIn residential electrical systems, a single circuit breaker (power feed) typically powers multiple wall outlets, and each wall outlet can power multiple devices (either directly or via power strips). For example: Circuit Breaker: F12-Kitchen-Outlets (16A)
Each wall outlet then powers one or more devices:
The ProblemNetBox currently allows a power feed to connect to only ONE device's power port. This means I can only connect F12-Kitchen-Outlets to KI-OL-01, and the feed becomes unavailable for KI-OL-02, KI-OL-03, and KI-OL-04. This doesn't reflect reality - the circuit breaker physically supplies power to all four outlets simultaneously. Current Workaround (Doesn't Make Sense)The only workaround would be to create separate power feeds for each outlet:
But this is incorrect modeling because:
Proposed SolutionPower feeds should support one-to-many connections to device power ports, similar to how:
This would allow accurate modeling of:
Benefits
The datacenter model (one feed → one PDU → multiple outlets) works for that use case, but home/residential installations are structured differently and equally valid to model in NetBox. Would appreciate hearing thoughts on whether this use case makes sense and if there's potential to support one-to-many power feed relationships in the future. Example hierarchy for clarity: |
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
-
Hi,
I'm struggling to understand how best way to record the power connections between our servers and PDU rails in the racks.
Environment
I have three racks across two datacentres. Each rack has two separate PDUs which (as I understand it) and feed by two different sources and protected by two different diesel generators in the event of a problem. ie, I have six PDU's in total.
I've tried the following strategies
Strategy 1
I created two Power Panels, one for each datacentre.
I then created six Power Feeds to represent the PDUs in the racks and assigned those to the correct Power Panel
This allowed me to record that (for example) Server A in DC 1 has PSU1 connected to DC 1 - Rack A - Left PDU and PSU2 connected to DC 1 - Rack A - Right PDU. However, when it came time to record Server B's (also in Rack A) power connectivity, both DC 1 - Rack A - Left PDU, and DC 1 - Rack A - Right PDU where greyed out.
At this point it dawned on me that maybe Power Feeds represent the individual plugs on the PDU.
Strategy 2
Deleted all Power Panels and Power Feeds and started again.
Created four Power Panels, two for each datacentre.
I then went to create 16 Power Feeds for Power Panel DC 1 - Left PDUs, with the intention of giving them names such as Rack A - Left PDU - Port [0-15] and it literally created ONE Power feed named
Rack A - Left PDU - Port [0-15], not 16 power feeds namedRack A - Left PDU - Port 0,Rack A - Left PDU - Port 1etc. ie, the Add a new power feed page doesn't support bulk creation like most creation pages seem to in Netbox.Manually creating the following four ports allowed me to record Server A and Server B's power connections. Result!, so now I just need to quickly and accurately create the induvial Power Feeds
Strategy 3
To save myself to finger effort I thought I'd import a CSV with the relevant information PDU names in so they're created consistently and less prone to typos. Using the following CSV to import Power Feeds...
... I get the following error...
Record 1 rack: Object not found: R203.The rack name is definitely R203. The slug is r203 and the id of the rack is 23. Using either the slug or the id in the CSV results in exactly the same error
Record 1 rack: Object not found: r203orRecord 1 rack: Object not found: 23.It's worth pointing out I don't know why
siteis a required attribute when bulk importing power feeds because it is not a field asked for at all (required or not) when creating a power feed manually.Am I doing something wrong (or even stupid) or does netbox have a bug in the import of power feeds?
Cheers
Steve
Beta Was this translation helpful? Give feedback.